We are getting a system alarm for high memory on an MD3 Display. 2 questions


1. What are the thresholds for this alarm ? We are close but below the specifications (according to the statistics, see photo)

Image 762


2. If we determine our application is functioning properly is there a method to remove this alarm, at least from displaying on the screen. Keeping it in the system log would be fine.


Thanks,

Mike

It appears 85% usage throws this alarm. Any ability to disable the alarm popup from the screen?

+1

The alarm for memory utilization will only show up if the System Information Channel for memory utilization is in the application and enabled. To avoid seeing it during normal operation, you can place this system information channel in a function group that you only enable when you log in as developer.

Disabling the channel will also prevent the log record in the system log.

+1

Outstanding. That makes perfect sense. Thank you.