XA2 Frequency Input sensor requirments
Keith Boone 9 years ago • updated by Gustav Widén (System support) 9 years ago • 0
I'm having issues with a flow sensor that does not work on the XA2 frequency input.   The manufacturer of the sensor is asking if the controller input requires a sourcing or sinking sensor.   What does the XA2's frequency input require?
Thank you
Satisfaction mark by Keith Boone 9 years ago
The XA2 frequency inputs are fitted with pull-down resistors, so they require the sensor to be PNP (sourcing) or push-pull.
See:
http://www.parker.com/literature/Electronic%20Controls%20Division/Literature%20files/iqan-xa2_instruction_book.pdf