DOUT OVERLOAD DETECTION ON XC43-M24 ON INITIAL START UP OF MC43

Todd F Reddick 3 weeks ago • updated 2 weeks ago • 6

Customer has XC43 via the main power disconnect. This also supplies two LS DOUTS. One of the DOUTS is expected to be on immediately on start up of MC43 (key on)and lights an LED. This is the only output that faults and only on the M24 version. MC43 is off until key is on. XC43-M24 presents with an overload on this DOUT when the master module is first turned on. Non M24 do not have this overload condition. Many machines in the field working with non M24. XC module has constant power until the disconnect is turned off. The unit is not started so we do not have a power draw. Key is cycled (Master power cycled while XC still has constant power) and the overload condition goes away. 100% 0f the time non M24 modules do not have an overload fault. 100% of the time M24 modules fault when master power is first turned on. Key can be cycled continuously after this initial power up and the M24 module will not fault out again until the main disconnect is cycled (power to XC cycled). Then the M24 version faults again when MC is first powered up. What is the difference between first power up and subsequent power ups of the Master module? The install guide states that the XC module may be started at the same time but not after. In this case it is powered well prior. i have talked with an RAE but he has not see this issue. Posting here hoping for some insight. 

Added a 500ms delay on the DOUT to resolve this issue. Guessing that the XC is detecting a false overload issue on startup and needs to see 0 command from the MC rather than a 1 to reset. 

Is this a firmware issue that will be resolved via an update? One would expect that there would be a Module Contact Interlock whereby IQAN does not allow a command output to be true unless it has established that the XC module is healthy. This would resolve the issue and not require a program variable(delay on) to resolve.

Or is this a customer issue where they need to now modify their program with this delay? Should all DOUT parameters that are required to be on at startup have a delay or just LS DOUT's.

This is undocumented near as I can tell. Is there any guidance available on how to implement an M24 variant correctly? Are there any other nuances we need to consider. The release had said other than moving to 7.03(now 7.06) that the M24 should be a drop in.

Hello Todd.

That DOUT circuit is one of the parts that was replaced on the M24 models.

We do always try to get the behaviour of the modules to stay the same when we need to change any internal components.

But it is not always possible to get the exact same when using new components.

The only thing i can thing of that could case any issue for you with the new chip is that it is faster to react when detecting an overload than the old chip. But we do have a higher threshold at the start for around 200 µs.

The higher threshold at start is meant for capacitive and incandescent loads, such as inrush into lamps. That should not matter for a LED.

But if you have a spike at the start that is longer that the higher startup threshold but shorter than the detection delay on the old chip i guess you could trigger the overload on the new but not on the old.

But that should be a timing of something like 100 µs or less.


Exactly what type of LED and how is it connected?

I tested a bit here with a LED here but for me it works without any issues.

Hi Thomas, I will get the LED info. It is part of an e-stop button. I just want to confirm your test scenario and that you are starting the XC-43 prior to the MC43. 

In an effort to explain what I thought might be happening please review below and comment. The customer has requested direction from Parker on how to correctly resolve this issue for them to continue using the M24 in production. The concern is that there are other hidden issues. Also do they implement a delay on just this one LS DOUT as it has the perfect recipe for this fault? 

What Happens on First Power-Up (Disconnect Cycled)

  1. XC43-M24 Initial Boot: When the main disconnect closes, the XC43-M24 wakes up into a "standalone" unconfigured state.
  2. Aggressive Protection On Boot: The newer driver circuitry inside the M24 variant performs severe off-state hardware tests to protect against internal component damage.
  3. LED Inrush/Leakage Conflict: An LED load represents an extremely low impedance at micro-voltages but pulls very little steady-state current. On first cold boot, the M24 driver runs an active startup diagnostic pulse. Because the MC43 has not initialized the CAN bus yet, the XC43 does not have its baseline application parameters to scale down its thresholds. It reads the unexpected electrical signature of the LED circuit during this blind test as a short-to-ground or an inrush violation, caching an internal Overload status.
  4. Immediate True Command: As soon as the MC43 boots up (key-on), it establishes communication and instantly commands that output to True. Because the XC43-M24’s internal hardware register is already flagging a cached startup diagnostic error, the output locks out instantly into an Overload fault state.

What Happens on Subsequent Power-Ups (Key Cycled, XC Keeps Power)

  1. XC43 Stays Initialized: When you turn the key off, the MC43 powers down, but the XC43 stays powered up via the main disconnect.
  2. The Logic Loop Remains Synchronized: Because the XC43 does not lose logic power, it does not re-run its aggressive, unconfigured, cold-boot hardware self-tests.
  3. Zero-Command Reset: Turning the key off drops the MC43 command to False (0). In IQAN architecture, an output must receive a 0 command to clear a cached driver error.
  4. Clean Boot: When the key is turned back on, the output starts from a clean, cleared register state and successfully transitions to True without running a conflicting startup pulse.

The Core Difference: Non-M24 vs. M24

The older, legacy XC43 modules used older semiconductor switches with looser analog diagnostic windows. They completely ignored the tiny electrical signature of an LED circuit during startup. The M24 version features ultra-fast, tight smart drivers specifically upgraded to satisfy stricter modern safety baselines (like IEC 61508 SIL), making them incredibly sensitive to initialization timing conflicts.

How to Fix It

Because you have a massive fleet of non-M24 machines in the field, you want a solution that works for both without altering the physical harness.

  1. Implement a Module Contact Interlock: Do not allow the MC43 to command the output to True until it has confirmed a healthy, stable CAN link with the expansion module.
  2. Add a Start Delay: In your IQANdesign file, gate the LED DOUT logic using a Delay On (TMR) block set to roughly 500 ms. This gives the MC43 time to boot, clear any cached standalone startup registers on the XC43 with a clean 0 baseline, and then safely assert the True command once the network is synchronized.

The led is a techna AC/DC 24V

The unit uses an internal current-limiting resistor of approximately 1.1 kΩ to 1.5 kΩ (typically around 1.2 kΩ). Because it is an active AC/DC circuit with a bridge rectifier and multiple LED chips, you cannot get an accurate reading of this resistor using a standard multimeter on the terminals.

Hello.

Yes, the XC43 is left running and then i start the MC43.

I am using 24V leds when i did this test.

The XC modules will not keep the output in the on state if it looses the connection to the master.

All outputs will go to 0 if connection is lost.

So it does not need a 0 command to the output when you turn the master off.

So the XC modules does not really have a "logic" that keeps running, it waits for commands from a master module.

I would say the easiest fix is to do what you already did and have a delay on startup.

Even if we did any changes on our end it would not be something that is fixing the problem for you now.

The XC output is not on or 1 in this overload condition. The module won't work when this happens. It is definitely 0. The issue is that the module has a fault on initial start up and requires a 0 from the master(I think).

Is the MC sending a 1 as commanded by the program IDC before getting a healthy report from the XC?

This presents as a firmware issue. The "fix" is done in one of two ways. Both present a 0 to the XC either by powering off the MC or by starting it up with a delay on the IDC for the DOUT. This points to the MC sending a 1 to a module that thinks it is unhealthy or the XC continuing to send an overload message until it sees a 0. The overload is a nuisance trip. 

Is the LED you are using AC/DC rectified? We can ship you a sample.

Does the XC do a self diagnostic when powered up with no master module? 

I was reviewing release notes and saw something on COUT sensitivity and critical fault detection fixed in 6.09.