Are Diodes or TVS required when using a COUT for On/Off control (NOT Proportional)

Mark Bevington 2 weeks ago updated by Tim Reen 2 weeks ago 1

Hi,

We are converting a machine that had MC2's, XA2's, XS2's & MC3's to use MC43's or XC43's. There were not enough DOUT's when the application was originally written, so COUT's were used and driven from either 0% to 100%, or from 100% to 0%.  There is no proportional control used.  The command input to the COUT is either 0% or 100% can instantaneously switch  from either OFF to ON, or ON to OFF at a 10 mS system cycle time. See below for an example of the code. Are TVS, or Diodes, required across the COUT to protect the outputs from instantaneous changes??   

Image 5210

Transient voltage suppression is not required on COUT channels. Often we see on/off valves where proportional valves may be implemented in the future, so we use COUT channels for on/off applications occasionally - and they work fine. The only consideration would be setting the maximum current for the on/off load to prevent saturation.