Are there any conflicts when using two identical master modules with the same IQAN address tag if they communicate only through J1939 bus?

Image 1854

GOOD, I'M SATISFIED
Satisfaction mark by Chris Litwin 5 years ago
Answered

This will work, as long as it is only a J1939 or a Generic bus you connect. 


Make sure to keep the Diagnostics buses separate. 

If you were to connect the Diagnostics buses of two masters of the same type with the same IdTag, IQANdesign and IQANrun will give you an error message about Duplicate module address found