Generic frame in channel (GFIN) reception issue

Paul Summers 3 years ago in IQANdesign updated by Gustav Widén (System support) 3 years ago 1

Hello Folks,

Has anyone had issues with receiving 11bit messages on a 29 bit generic bus (application is written in 5.03)?

I have 3 messages that I know are being broadcast (here is a capture from a separate sniffer I used to verify);

Image 2625

But all three of the GFINs are not reading... I have tried entering the identifier in both decimal and hexadecimal without success;

Image 2626


Any ideas on how to resolve would be greatly appreciated!

To read messages with 11-bit identifier, you must configure the generic bus with standard identifier size.

If you have both 11 and 29 bit identifiers, you can configure one generic bus with standard identifier and one with extended, and move them in IQANdesign to be on the same physical bus.