cin simulation
Ed Schippers 5 years ago in IQANsimulate • updated by Gustav Widén (System support) 5 years ago • 1
I'm having some strange problems with simulating a CIN channel.
setting:
min: 4000 uA
max 20000 uA
scaled min 0
scaled max 1935
when simulating, the slider will not move within the 4000/20000 or 0/1935 range but between 1935 to 77400.
Design and simulate 6.06
It sounds as if the channel might be adjustable, and that you are simulating old calibration points.
To see the raw value, place the channel in a simulation group in IQANsimulate and select Full Value Range.
To see and change the calibration, connect IQANrun to simulator and check the adjust group.
The values you have match what you would see if you have it calibrated as 0 uA to 100 uA in your simulation.