We have 12 values being logged every second, and I have downloaded the log to find that every 4 minutes and 15 seconds the time counter resets back to 2 hours and starts counting again at 02:00:00. Weirdly earlier results (an earlier index number) also appears to have the same behaviour around 01:00:00 and then it strangely jumped to 02:00:00. It then continues to go back to 02:00:00 every 4 minutes 15 seconds.
I understand the MC43 does not have a clock and we know start 154 is the information I need to extract, but I would have expected the timer to begin at 00:00:00 and carried on counting up until the ignition was cycled and log stated 'Start 155'.
Can I assume they are all in the correct order based on the index value rather than the time? ie. greater index value = most recent log and timer counting is not relevant?
See below a similar record earlier where it jumps from 01:00:00 to 02:00:00:
The log is set to recycle so can hopefully discount filling up the controller and it not being able to handle the quantity. This log is set to occupy 95% of the log memory.
IQAN 6.08.
Customer support service by UserEcho
There was a problem in 6.08 and 7.00, fixed in IQANdesign 7.01:
Sort on index to see chronological order.
Thanks, I will update the system to 7.01.