Critical Error codes for XC43-M24
I have a new XC43-M24 running on 7.05 and it is flashing 4 red and 2 yellow, followed by a series of yellow flashes, 4-1-3.
I can see from the user manual that the 4-2 code means Critical Error but I don't have a reference for the detailed blink code that follows. Can you tell what this error code is? & Can you post a detailed Error Code reference in this forum?
R4:2 4:1:3 is a FW update error.
It will happen if the master module runs version 7.05 and the XC4-M24 is secure boot.
Is there a fix for this?
Is it in secure boot if the id tag is not connecting?
No, that is safe mode (starting without loading the application).
Secure boot is that a signed firmware is required for installing on modules produced with secure boot.
Secure boot was introduced in 7.06.
This was put in production 2026 week 24 for MD5 and week 25 for the C4-M24 family.
Units produced with secure boot can not be downgraded to a version that does not have it.
The key is hardware coded in to the unit in production and can not be changed after that.
The fix is to update the master to 7.06 so that they have the signed firmware the XC4 is looking for.
As you have it the master is trying to update the firmware on the XC4 with what it think it should have but the XC4 does not accept it because it is not signed.
Thank You.
I was able to advance to programme to 7.06 and it took.the update.
What serial numbers did the Secure Boot hardware start with?
If you look at the serial number the first two are the year and the second two are the week.
so for MD5 it is serial numbers starting with 2624 and later and for C4-M24 it is 2625.