Cout as digital Out
christophe 7 years ago
in IQANdesign
•
updated by Ulrik Zakariasson (Software development) 7 years ago •
2
Hi,
I want to use an Current Out channel as Digital Out ( run out of channels )
Wich function can i use to convert the on/off signal to on= current @ 100% and 0=current @ 0%?
Answer
Answer
Use a dual channel:
You can use also both solenoids, but not at the same time. You need some interlocking, here is one way to do that:
Hi,
Maybe you can juste use a Math function, with the followin Q-Code :
if DIN-A = true then
Result := 100
elseif DIN-B = true then
Result := -100
endif
Or if you use just one Digital Out :
if DIN-A = true then
Result := 100
elseif DIN-A = false then
Result := -100
endif
Customer support service by UserEcho
Use a dual channel:
You can use also both solenoids, but not at the same time. You need some interlocking, here is one way to do that: