0
Answered
MD3 and MD4 Operating temperature
Kerim 7 years ago
in Master modules / MD4
•
updated by Gustav Widén (System support) 7 years ago •
4
Hello
in Catalogue of MD3 for operating, ambient -30° to 60°C (-25°C>LCD off>75°C)
in Catalogue of MD4 for operating, ambient -30° to 70°C
What is the lcd-off range of md4 screen?
Thank you in advance for your helps.
in Catalogue of MD4 for operating, ambient -30° to 70°C
What is the lcd-off range of md4 screen?
Thank you in advance for your helps.
Customer support service by UserEcho
Also note that in the MD4 instructions, there are two temperature ranges stated.
http://www.parker.com/literature/Electronic%20Controls%20Division/Literature%20files/IQAN-MD4_instructionbook_HY33-8408-IB_UK.pdf
Ambient temperature -30 to 70 °C, this is the recommended ambient operating temperature.
Storage temperature -40 to 85 °C
What these numbers don't reveal is that especially in low temperatures, it is the storage temperature that is the important number for avoiding damage to the display.
Starting up the display at -40 °C is not really damaging it, but the MD4 display may not be usable until it is > -30°C.
At high temperatures, you will be able to use the MD4 display outside of the operating range, but colors may not be correct. Also, when combining high temperatures (outside of the operating range) with moisture, there can or will be damage to the display.
The MD4 +70°C is given as the recommended maximum ambient (surrounding) temperature, to have margins to the display component temperature, since component temperature will be higher than ambient.
But you can switch on the MD4 at -40°C. The MD4 will start, but the display won't be readable until the heat geneated gets it to about -30°C.