Using two(2) or more low side outputs in parallel on XC-23
Guillaume Fournier 6 years ago
in Expansion modules / XC2x
•
updated by Gustav Widén (System support) 6 years ago •
1
Hello,
I'm wandering if I could use two(2) or more low side outputs in parallel on the XC-23 to increase the carrying current capacity from 300mA to 600mA (2 outputs) or more. I have a relay that I need to drive that needs more than 300mA.
Thanks,
Guillaume
Customer support service by UserEcho
Yes, it is possible to parallel connect the XC23 low-side outputs. Note that you must not exceed the combined load for the group, see Appendix A in the XC23 user manual :