0

XC43 COUT Open Load Threshold

Chris Litwin 3 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 3 years ago 1

What is the XC43 COUT open load threshold when the COUT is off?

The off state error detect is in the range 20-50 kOhm, same as for a DOUT. 

But unlike the DOUT, the COUT always have a minimum load current when on, so you cannot actually use the COUT for driving loads with this high resistance.