Digital out low side outputs

Nicolas Francoeur 2 years ago in Master modules / MC4x updated by Gustav Widén (System support) 2 years ago 1

Is this MC43 output configuration is correct?

Can we power a load at higher voltage than the MC43 power for output 30 to output 46?

Image 3629

GOOD, I'M SATISFIED

very thanks for the answer.  

Satisfaction mark by Nicolas Francoeur 2 years ago
Answered

Yes, the MC43/XC43/XC44 Digital out LS outputs can be connected as shown. 

The module +BAT supply does not matter for connection to these low-current low side switches. 

The important parameter is voltage in relation to module ground.