More (HS)* (LS)* MC43FS
Dartagnan Léonard 11 months ago
in Master modules / MC4x
•
updated by Gustav Widén (System support) 11 months ago •
3
Hi,
I have a applciation with alots of safety control Dout.
Like i could read a the page 97 and 99 of the instruction book manuel of the MC43FS.
We can have 5 Dout.
In safety function we need to combine one HS and one LS pin to a output.
In Dout i have acces to 5 direcly and would need 6.
I would like to know if it is possible to use the pin C2:71 HS and combine with a other LS for example C2:16 ?
Else my other solution would be to use Cout as a ON/OFF signal output unidirectional.
Thanks
Dart
Customer support service by UserEcho
Unfortunately the output combinations on MC43FS are fixed.
The solution will have to be to use a COUT.
Like i can reed in the instructionbook in page 88 of MC43FS.
A Cout can be use in safety fonction for activating a ON/OFF coil.
If this is respected (See image) ?
Do you have more condition to respect ?
I need to be sure i respect all the SAFETY FUNCTION requirement in my application.
Thank for your time !
Correct, the current range must be respected. That means on-off valve coils should be fine, while relay coils could be a problem.
In the regular case where a COUT is used for proportional valve, it is common to have it adjustable so then the rules for limits and access protection of adjust items will apply. For an on-off application of COUT, this could be easier to handle by setting fixed currents in the application.