XC43 DOUT HS in parallel
Jamy 6 months ago
in Expansion modules / XC4x
•
updated by Gustav Widén (System support) 6 months ago •
1
When connecting loads to high side digital outputs in parallel, the manual says on page 96 "Increased drive capability
Power driver high-side is connected in parallel with adjacent output to drive double
load current." On page 116 it states the max load per output is 4 amps and max load per group is 6 amps. So when you connect in parallel is the max load 8 amps? Or 6 amps?
Customer support service by UserEcho
6A if you use digital outputs from the same group.