VIN voltage drops
Lars Bolduc 2 years ago in Expansion modules / XC4x • updated by Gustav Widén (System support) 11 months ago • 2
I have an odd issue, maybe power or ground reference related.
XC43 IQAN 6.08, sensors powered using the main 24VDC not regulated VREF.
When I start driving valves with the module the reported voltage from my VIN sensors drops by up to 5%.
It happens to all of them irrespective of the sensor type.
It also jumps around a ton.
This makes a huge difference on my 0-5800 0.5-4.5V sensors.
200+ PSI, not good for sensor accuracy.
Any ideas of what to try to fix?
Regards,
Getting the same exact error on my MC43. Havent found a fix yet
It sounds as if there may be a difference in ground level between the sensor and the XC43.
With 5V sensors supplied by +VREF and -VREF, you normally avoid such problems.
For this case with a 24V supplied sensor, a consider using -VREF for sensor ground.
Just make sure the external sensor + supply has a small enough fuse to not burn the -VREF traces in case there is a short across the sensor.