Heartbeat

Serge Rudziankou 2 days ago in Master modules / MD5 0

Hello,

I am working on a hydraulic control system based on MD5 and MC43. The main control logic runs in MC43, while MD5 handles non-safety UI functions.

To ensure safe operation, I implemented a simple heartbeat between MD5 and MC43:

Setup:

  • Heartbeat: digital signal toggling TRUE/FALSE every ~100 ms in MD5
  • Transmitted via J1939 to MC43
  • MC43 monitors time since last change
  • System cycle time: 50 ms
  • Safety action: if no change for >500 ms, MC43 disables outputs
  • Logging is active on both MD5 and MC43

Problem:

The heartbeat signal is periodically lost or appears frozen for short periods (typically 100–3000 ms, sometimes longer), triggering safety shutdowns.

Test setup (minimal system):

  • Only MD5 and MC43 connected
  • 30 cm CAN cable
  • Two 120Ω termination resistors at both ends
  • No other CAN nodes
  • Minimal application: only one J1939 message + heartbeat logic
  • No HMI logic or additional communication

The issue still occurs in this simplified configuration.

Tests performed:

  • Different CAN speeds (including 250k / 500k/1000)
  • J1939 and generic CAN communication modes
  • Same behavior observed across configurations
  • No communication errors reported in internal Parker logs

Question:

Has anyone observed similar intermittent J1939 communication drops between MD5 and MC43 under otherwise stable conditions?