Heartbeat
Hello,
I am working on a hydraulic control system based on MD5 and MC43. The main control logic runs in MC43, while MD5 handles non-safety UI functions.
To ensure safe operation, I implemented a simple heartbeat between MD5 and MC43:
Setup:
- Heartbeat: digital signal toggling TRUE/FALSE every ~100 ms in MD5
- Transmitted via J1939 to MC43
- MC43 monitors time since last change
- System cycle time: 50 ms
- Safety action: if no change for >500 ms, MC43 disables outputs
- Logging is active on both MD5 and MC43
Problem:
The heartbeat signal is periodically lost or appears frozen for short periods (typically 100–3000 ms, sometimes longer), triggering safety shutdowns.
Test setup (minimal system):
- Only MD5 and MC43 connected
- 30 cm CAN cable
- Two 120Ω termination resistors at both ends
- No other CAN nodes
- Minimal application: only one J1939 message + heartbeat logic
- No HMI logic or additional communication
The issue still occurs in this simplified configuration.
Tests performed:
- Different CAN speeds (including 250k / 500k/1000)
- J1939 and generic CAN communication modes
- Same behavior observed across configurations
- No communication errors reported in internal Parker logs
Question:
Has anyone observed similar intermittent J1939 communication drops between MD5 and MC43 under otherwise stable conditions?