I have a question regarding coils for proportional valves controlled by uni- or bidirectional COUT outputs:
As of now, we are using the coil "Sun Hydraulics 770-924" for some of our proportional valves. That coil includes a TVS-diode:
Image 5428
That contradicts the (somewhat loose?) statement in the MC4x Instruction book:
Image 5429
I understand that there is some kind of diode solution internally in the MC4x for COUT's. Does that solution make the coil's diode solution redundant?
Some information regarding the coil:
Image 5431
Image 5432
The coil _appears_ to work just fine in our application but I haven't checked it with an oscilloscope during operation to see what is actually going on. Maybe the TVS-diode in the coil is never active?
In short:
Is it OK to use this coil or does it, in some way, interfere with functionality? Or should I interpret the Instruction Book strictly and use a coil with no diodes at all?
I thought that with your knowledge of the MC43's internal hardware perhaps you could shine some light on the matter?
Much appreciated,
The COUT has an internal circulation diode as can be seen on page 89 of the instruction book.
Image 5443
An external diode will influence the current measurement and not give as good results.
But you will not be damaging anything in the module.