Newbie On Switching Values

Carl 8 years ago in IQANdesign updated by Ulrik Zakariasson (Software development) 8 years ago 4

Hi Guys,


Newbie here, was CodeSys, now starting IQan.


I have a project where I have two values (Two 5v sensors) operating all the time and I want to send the value of these over can on the same SPN etc but the one to send is requested by another SPN.


So I have sensor A and sensor B. Both use the same SPN 2927.

When SPN 3928 received equals 1, Sensor A value is sent on SPN 2927. When SPN 3928 equals 2, Sensor B value is sent on SPN 2927.

What do I use to set which value is be sent on receiving the SPN?



Cheers,

Answer

If I understand this correctly, you have two sensor inputs coming in on VIN channels.  You wish to output one sensor value or the other onto the J1939 bus based on the value of a J1939 input parameter.  You can only read SPNs, so if you want to send a J1939 CAN message, you will need to use the JFOUT channel and populate it with JPOUT parameters.  The input to the JPOUT parameter can then be a MATH channel with the appropriate logic to select the desired sensor value.


0
Answered

SV Camera into MC43 on MD4/MC43 multi-master system?

David Holcomb 8 years ago in IQANdesign updated by Ulrik Zakariasson (Software development) 8 years ago 3

I am curious if SV cameras can be used on a multi-master application, where it could be wired into ethernet port on an MC43 and shown on a MD4 ?  

This would be a multi master system with master and diagnostic busses between MC43 and MD4.


0
Answered

MC43 COUT.... V4 limit is 2500mA, but V5 is capped at 2000?

David Holcomb 8 years ago in IQANdesign updated by Ulrik Zakariasson (Software development) 8 years ago 3

Building a project with an MC43. 


In design 5, it seems that the limit for a COUT is 2000 mA.

In design 4, i can set it up to 2500 mA.   


1.  is there something that I'm missing  for setting it up to 2500? 

2.  is there any way to 'parallel wire' and run multiple COUTs? 


Thanks


0
Answered

Newbie, memorize Channel Help

Carl 8 years ago in IQANdesign updated by Ulrik Zakariasson (Software development) 8 years ago 2

Hi Guys,


All new to IQAN so sorry for the simple questions but have to start some where.

I am doing a project where some options are to be stored either true or false.

The message comes via CAN J1939 and then an SPN. So I have two options, both on two different SPN's and I want them to be memorized and stored where when one is received as true (01) then the opposing option memorized will go false. There wont be a part when both SPN's are received as true

 (01).

I simply added the two memorizing channels to the look at the SPN's and set to "STORE". the "Reset Value" was the opposing memorize channel. But nothing works?

0
Answered

soft start time[ms]

Supratim 8 years ago in IQANdesign updated by Jan Gillesen 6 years ago 2

In DOUT there are two functions.

One is Delay on [ms] or Delay off [ms] & the other is Soft Start time [ms] or Soft stop time[ms].

what is the physical effect of Soft start or Stop when we are operating a relay. As per our understanding it will ON or OFF when it reaches the required voltage. So it may be usable for some other load but for any relay or solenoids has it any effect?

Answer

The DOUT Soft Start function is ment to be used when energizing solenoids valves, when you need to create a more soft switching of valve and actuator behind the valve. (Prevent Bang-bang switching) . 
Soft start should NOT be used for energizing solenoids of relays, as a relay needs to switch fast to prevent contacts burning. 

The Peak and Hold function you could use  also for (larger) relays, engergize solenoid with full power, than reduce PWM current to reduce current consumption.
  

0
Answered

​Ability to adjust FP via MD3 buttons or MD4 VDIN without accessing FP adjustment screen.

Pawel Pekala 8 years ago in IQANdesign updated by Gustav Widén (System support) 8 years ago 3

Ability to adjust FP via MD3 buttons or MD4 VDIN without accessing FP adjustment screen.  

Image 866

0

Industrial Style Push buttons

Caleb 8 years ago in IQANdesign updated by Pawel Pekala 8 years ago 0

Hi guys,


I have been working with IQAN MD4s for a little bit now and I am curious if there are any developments in making push buttons for the MD4? I typically use industrial type HMIs but we have been starting to use the MD4 for the environment aspect. In a particular application I am working on now, it requires the HMI to have some push buttons for the operator to have some control through the screen. It would be nice to have a few options of pre-installed buttons so I can assign some internal digital registers. 


What I had to do to get around this was create my own bitmap buttons, import them in as images, create virtual digital inputs, and use the custom button with my made images to act as a button. It was a little cumbersome and tedious so I thought that would be something really helpful to implement into a rev of IQAN 5. 


Hope this is an idea that will be considered. 


Thanks!


0
Answered

Update program dispay

Jon 8 years ago in IQANdesign updated by Ulrik Zakariasson (Software development) 8 years ago 3

Hey guys, I currently have a application completely developed for the MD3, I would like to take this to the next step and start using it with the MD4-7.


What would be the easiest way to do this, keeping as much as possible and basically just rebuilding the screens/interface. I plan to do this using Iqan Design 5 as I really like some of the new features.


Sorry if this seems to be a simple question, I've just never had to do it before (always been a complete new application).

0

Linear Bar Control Issue on MD3 Display

Doug Coutlee 8 years ago in IQANdesign updated 8 years ago 3

I am trying to add a Linear Bar Control to an MD3 display page and set the Orientation to vertical instead of horizontal. All of the versions of IQAN Design newer than 2.63 will not let me make the a Linear Bar Control vertical on a MD3 display page. Is this a bug?

0
Answered

Bidirectional Prop. Valve input

christophe 8 years ago in IQANdesign updated by Gustav Widén (System support) 8 years ago 2

I have an MD4-5 and XC-21. Another measurement system gives output for 2 bidirectional prop valves. (24V 3Amax.) how can I measure this values with one of the modules?
The max current in is limited to a few Mili amps and the voltage in is limited to 5vdc.
PWM could be an option but there ate only 3 available on the xc21


Tips are welcome!