MC34FS Module Dropout On Update

Kevin 2 years ago in IQANdesign updated by Gustav Widén (System support) 2 years ago 2

We have a system with 1 x MC43FS, 1 x MD4-7, 1 x XC21 and 2 x MC41FS, running 6.08.30.8216.

On MC43FS we have 2 x CAN Open encoders on CAN Bus E that are sending PDO and heartbeat information as soon as we apply power. These are configured to run at 125kbps. We established that when updating the project it would update all the modules except MC43FS which hangs and crashes out. It seems to begin updating the MC43FS module (does it last in line after all the others), but stops halfway through and crashes out. System has to have power cycled and screen says no application and have to reload the software. Occasionally it will load in, around 10% success rate. When it drops out i get flash 'no application available' as in instruction manual.

Unplugging one encoder and IQAN will allow me to update the system including the MC43FS with occasional dropout.

Changing the bus speed of the encoders has improved it, seems to allow me to update the system with both encoders connected smoothly, occasionally hangs but significantly better.

Is there an interaction between the MC43FS firmware and speed of CAN devices? We had this issue a few years back on a MC3 and that was conflicting speeds on firmware check before boot. Seems it may also be present on these newer modules?

Weirdly also it says 6.08.24 for the MC43FS, however we are using 6.08.30. I noticed the IQANDesign 6.08.30 only has this for the MD4 and not the MC43FS, which mislead me somewhat when trying to establish the fault.

Image 4001

Image 4002

0

LC5 query

Ash 2 years ago in IQANdesign updated 2 years ago 2

Are there any example programs for the LC5 joystick?


Currently utilizing the 2007699 (lc5-c01-mpb2w2t1) joystick

using iqan design 6.02. I get the LC5 and link it to an MC43 on system layout but how do i get the axis outputs and button digital io? I can find no EDS file or instructions as to PDOs for the outputs?

Thanks in advance

0

Impicit value type conversion

Grisel, Evert-Jan 2 years ago in IQANdesign updated by Gustav Widén (System support) 2 years ago 6

Since version 7 I get a "Impicit value type conversion" warning when I use a Derivative function in the activation part of a value log item.


Does anyone have a idea how to solve this?

Image 3952

0

IDC Delay on / off time limit

Grisel, Evert-Jan 2 years ago in IQANdesign updated by Gustav Widén (System support) 2 years ago 1

Why is the IDC delay on / off time [ms] limited at 3276750 in version 7

(and unlimited in version 6)

0
Answered

XC43 PWM out HS+LS internal free wheeling diode

Shannon Tyler 2 years ago in IQANdesign updated 2 years ago 2

We are swapping out from the XA2 to the XC43 and we originally thought we were going to be using the PWM HS output so we attached a ark suppressing diode on the 4-way 3-pos cart valve (HSP 10-47CB-0-v-24ER). We however ended up using the PWM HS-LS output which has a internal free wheeling diode. Is the newly installed ark suppression diode going to case problems down the road. and is it best practice to just use the internal diode on the PWM HS+LS output?

0

IQAN D6 Corporate licence expires soon

Angela Conte 2 years ago in IQANdesign updated 2 years ago 2

Hello, our corporate D6 licence expires 11/06/2023. if we do not renew, what is the impact to our users?   We do not want to go to version D7 just yet.   We want to make sure that we can still use the current version. Please advise.

0

Issue with JFOUT sending to a DA

Kerry Brock 2 years ago in IQANdesign 0

I am having an issue in IQANdesign 7.00 when I set the destination address in a JFOUT channel to either "Assigned Module" or the actual SA number.  I get a "No Contact" message.  When I use IQANanalyze I can see the CAN frames from both the IQAN master (MC43) and the third party device.  If I set the destination address to a value not used by any other module on the bus, I no longer get the "No Contact" error and I can read the CAN messages sent from the third party module.  The CAN structure of the message is a little odd to me, as messages from both the IQAN master and the third party module use the same PGN number, 61184 to send information between the two modules.  This structure is part of the CAN protocol used by the third party device.  I cannot figure out a way to send a CAN frame (JFOUT) to a specific SA without getting the "No Contact" error.  I even tried changing the "J1939 source address" line in the JFOUT to 39 instead of "Default" and it did not seem to affect the "No Contact" error.

0

qcode MAC channel - MinOf multiple if else statements

Pawel Pekala 2 years ago in IQANdesign updated 2 years ago 2

How to run MinOf function within MAC channel using qcode if multiple if else statements are used? 

Example:

[1] If ......... else .....

[2] If ......... else .....

[3] If ......... else .....

[4] If ......... else .....

[5] If ......... else .....

[6] If ......... else .....

MinOf ([1],[2],[3],[4],[5],[6])

Is this possible with qcode using just one MAC channel?

Thank you 

0
Not reproducible

Difficulty sending programs to new MD4s running 6.08.28

Matt 2 years ago in IQANdesign updated by Gustav Widén (System support) 2 years ago 4

I'm frequently seeing issues sending programs to brand new MD4s which are running firmware 6.08.28. The main issue I'm seeing is messages saying no reply from master module. Yesterday I had one brand new module where I tried sending a blank project from iQAN design 6.08.30 several times before it went in.

We only ever send projects to the modules over a direct ethernet connection. This is occurring with different cables and even when sending projects using iQAN run. Is this a known issue?

0
Answered

Multimaster No contact error with external module connected to both master but works

A DOMS 2 years ago in IQANdesign updated by Gustav Widén (System support) 2 years ago 3

Hi,

I'm using two MC43 that are both linked to a remote controle(generic) by canbus B.


Image 3934


I have a display on my remote and I can send information through 4 RPDO to show data on the remote screen.

It's working well from my master MC43[0], but when I send my canbus messages from the MC43[1] I have a "no contact" error message that appear BUT the crazy thing is, I still receive my data on my screen !


Image 3935

Image 3936


I see the data on the screen and I see it also with PCAN-View :

Image 3937


So the data is sent, but my master think there is no contact.

I had the same problem before with my both MC43 calculators and a MD4-7 that was in the project.

I had some touch buttons on my MD4-7 screen and when I sent the data from MD4-7 to masters, It was OK with MC43[0] but no contact with the MC43[1], BUT I still receive the data.


Is there something wrong on my multimaster system ?