0

XC-43 Modules Leakage Current/Voltage

Jamy 4 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 4 years ago 1

The Leakage Current/Voltage from the Digital Outs make it difficult to control LED's and Audible Devices without using a relay/resistor/other.  The Leakage Current/Voltage is also making it difficult if the Digital Outs are read by other electronic devices (off is not off).  How does Parker recommend interfacing with these devices using the new XC-43/series modules? Adding external devices to these circuits is making the XC-43 modules not very convenient.

0
Completed

XC43 Flashing normal (yellow) with CAN-BUS no contact error on master module and in IQANdesign.

Jamy 4 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 7 months ago 3

I've got two XC43's on a machine. One on CAN-BUS-A & the other on CAN-BUS-B. Both modules are flashing yellow normal operation but the master module says A-BUS no contact & B-Bus no contact. When I run the program in IQANdesign connected to the machine, I also see no contact on both modules.

Why are the two XC43 modules flashing the normal operation flash code and not the CAN error/no contact error flash code?

0
Answered

XC44 HS+LS Overcurrent Update

CalebD 4 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 3 years ago 3 1 duplicate

I am still unable to reply to previous posts with the same error being reported as before when I attempt.. 

In reply to Gustav's comment on this post: XC44 HS+LS Overcurrent Follow Up / Hardware / IQAN

"Ok, the disabling of the function group explain at least a part of the behavior you see.

When disabling the FG, the DOUT deactivate. Diagnostics is still running, so when disabled all checks for output off are running. In IQANdesign you will only see channel status disabled though.

At what events do you disable? Only before cutting the highside externaly?

Or also during normal deactivation of the output?"

The function group is only disabled on Estop. Before an estop event the output functioned as normal, the estop being triggered starts the overcurrent issue. 

Original post: XC44 HS+LS Overcurrent / Hardware / IQAN

0

XC43 COUT Open Load Threshold

Chris Litwin 4 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 4 years ago 1

What is the XC43 COUT open load threshold when the COUT is off?

0
Answered

XC43 PWM Output voltage jumping from 6V to battery voltage randomly

Tyler Helmus 5 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 5 years ago 1

I'm having an issue where the PWM outputs jump in voltage to battery voltage seemingly randomly and with no change in the displayed output on IQAN run. Anyone know what is going on?

0

XC42 Analog Input Pin#8 Internal Short?

Arbutus 5 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 5 years ago 1

We had a XC42 where we use a hall effect analog device that was mapped to pin 8 and configured as an analog input. The device was connected to Vref A so uses a supply voltage of +5v and provides 0.5-4.5v thru 180 deg of rotation. We first started to see it only indicating from 2.5-4.5v and then eventually we got fixed values that fluctuated based on if the hall effect magnet was present or not. After some trouble shooting we removed the wire from pin at a connector and were getting a fixed voltage of around 4v at pin 8. With this removed the magnet rotated gave us 0.5-4.5v at the output of the sensor.

A data sheet of the sensor is attached. Model # is RTP180LVNAA

We ended up remapping the input to pin 52 and it all worked fine again.

It almost seems like the pull up resistor in the channel was "turned on"???Honeywell RTP Sensor

0
Answered

Outputs Missing in IQANDesign

Lars Bolduc 5 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 5 years ago 3

I've noticed that the following XC43 pins appear inaccessible via IQANdesign:

C1:61

C1:62

C1:63

C1:64

C2:69

C2:70

C2:71

C2:72

Is this by design or am I missing something? They're listed as PWMOUTs or High Side DOUTs in the manual.

IQANdesign 6.04.5.5888

I have not checked the other XC4x modules.

0

VREF error on XC43 Enable

jolynik 5 years ago in Expansion modules / XC4x updated 5 years ago 10

Working on a project in which 2 XC43 modules are not supplied with power until the MD4 commands a safety relay contactor closed.

I've worked through almost all the bugs, but I'm getting a VREF A error as soon as the XC43 modules enable. I've tried leaving up to a 30 second delay after powering the XC43 modules to enable them, but the error still pops up for one cycle and then shows up on screen (Watching in a measure group, VREF starts at 0V for one or so cycles, then goes right to 5V). All the sensors read fine, just have the error at system start.


Is there any way to delay how long it takes for the VREF error to show

0

xc43 referance voltage

Ed Schippers 6 years ago in Expansion modules / XC4x updated by Cristian Ramirez 4 years ago 5

On the XC4x serie there are multiple Vref+ and Vref- and on both C1 and C2 

Are these interaly connected in the module? 

Or are they seperate from eachother and serve only dedicated Vin's?

Best Regards Ed

0
Answered

PWM OUT HS to control proportional valve "D1FBE01HC0NJJ3"

Hassan 6 years ago in Expansion modules / XC4x updated by Gustav Widén (System support) 6 years ago 2

I'm using the expansion module XC43 to control valves, usually, I use Cout to control proportional valves but I run out of current output pins " I have 13 valves" I'm wondering if I can use PWM OUT HS to control D1FBE01HC0NJJ3 " Proportional directional valves in general " also L90LS, P70? Because it seems for me that PWM is only to control pulsar valves that have some frequency working value.