COUT open load error calculation
We have a machine that has sporadic nuisance open load errors on a function controlled by a unidirectional current output (COUT-G) on an MC43. Since this happens with some frequency, I suspect we are right up against the limit of the open load detection threshold. They test out well in assembly, but any increase in resistance occurring in the field might be setting it over the edge of the error threshold.
How can I calculate at what load resistance, commanded current, and supply voltage an open load error will occur?
This function is controlled with a Parker CCP024H 1/2" super coil with nominal resistance at room temperature of 30.30 ohms. Machine runs on 24V (around 28V when alternator charging). Maximum commanded current is set to 600mA.

Using Current Out as 4-20 ma signal for VFD
Are the current out channels on an MC43 suitable for dishing out a 4-20 ma signal? It would be controlling a VFD.
I know the current out channels are typically used to control valves and used in the hundreds of milliamp range.

COUT overload error when PWM HS is shorted to GND
We are using a MC43 and using PWM and COUT channels. What we have noticed is when a PWM HS output is shorted to ground, one of our COUT outputs goes into overload. In our case, C2:51 was shorted to ground but C2:67/C2:15 had the overload error.

ID-Tag 4-7 for Molex MX123
Hello,
ID-tag 4 to 7 does not exist for Molex MX123.
We use 4,5 and 7 today and have to re crimp those ID-Tags for MX123.
When do you plan to offer ID-Tags 4 to 7 for MX123?
Regards
Fredrik Forsberg

MC4X CAN bus labelling different in manual and IQAN Design
IQAN Design refers to CAN bus on the MC4X as A, B, C etc, manual (under installation) refers to it as numbers 1, 2, 3 etc. Although its obvious to work out, its better for us if its one designation across the board to avoid confusion when cross referencing documents.

MC41 losing CAN comms
We are using a MD4-7 and x2 MC41's on some of our machines (we actually wanted to use only x1 MC42 for these jobs but we are still waiting for the parts to arrive and have deadlines to meet so we are just using what we have available to get the job done)
But last night we started testing the machine and went through all of the procedures and functionality when all of a sudden an error appeared on the display telling me that one of the MC41 controller lost comms, but the other one was still fine and giving readings... So the 1st thing we tried to resolve this was typically switching the machine off and on, but this time there was no CAN comms at all.
We went though the wiring harness and made sure that everything was correct and the wiring was all good, so we then went and replaced both these controllers with new MC41's we had in stock, we plugged it in uploaded the software and the system was happy again with the new controllers and it is still working fine at this moment... So I took the 2 faulty MC41's to my office and connected it all together to try and diagnose the issue.
Each time I tried uploading software (using IQANDESIGN 5.01 via ethernet) it kept on warning me about the incomplete system and that only the MD4-7 will be updated.
Eventually we switched from CAN-A to CAN-B only on the MC41's. but upon each attempt to upload the software, the same "incomplete system" warning appeared.
So I just left it for a while and a few minutes later decided to just try again uploading once more. Well it worked all of a sudden and that is also a big problem, because I didn't change anything where I could say " there, that was the problem".
This is worrying us a bit, because we have no idea why this happened in the first place and secondly these machines are going to the middle of Africa... So this sort of thing must not happen at all!
I have only been using MD4's and MD3's with XA2's in the past without any problems at all, these are our first machines using the MC4x family and this is also the 1st time that I encountered any issues like this on IQAN.
Have anyone else experienced this before? I have no idea why it failed or why it started to work again and this is definitely not the correct answer to give the person asking this question when there are deadlines to meet.
The other thing to mention also is the LED's on the controllers which blinked bright yellow 3 times then blinked dimmed yellow 3 times while it was not communicating. which also does not correspond with these fault codes in the manual. There was no RED LED blinking at all.

HS+LS output EMF capability
Would like to use the HS+LS configuration to control the HV contactors in an Hybrid configuration. I am reading note about using Diode to protect against EMF. But I cannot find specification on acceptable EMF level? Our contactors have built-in EMF clamping diode rated at 150V?
Also how does the open circuit detection in an off state works? injecting a current i am assuming. How much? Just want to avoid issue with Dropoff voltage for the coil.

Driving Pulsar with the PWM on MC43
Hi There,
Hope all is well,
Is there any possibility to drive Proportional 24v 33Hz Pulsar valves with the PWM outputs from a MC43 ? Reading the manual it states that this will not work from MC43,but reaching out to see if it is possible.
ATM I am using the proportional flow from the pump and making the Pulsar more like an ON/OFF, This is working currently but would like to use the Pulsar proportionally.
Thank you

MC4x/XC4x 12V 30W solenoid overload error
What is the suggested solution for driving NG6 valves with standard 30W solenoids at 12V system voltage with MC4x/XC4x modules?
We use the HS+LS digital outputs for driving Parker D1VW valves with "K" code solenoids in a 12V system. As stated in the instrucion book, max load per output is 2.5A, but the measured current is 2.7A (as in the D1VW catalogue). The measured solenoid resistance is 5 Ohm, but it should be within 7-14 Ohm (MC4x/XC4x instrucion book).
30W solenoids are standard at other valve suppliers too, so changing the valve isn't an option. Change the system voltage to 24V also isn't possible for this project.

MC41 - M18-4 Barrel Speed sensor
Hi,
I have an MC41 module and I want to pick up the signal from a speed sensor M18-4VPFF200-Q8.
I want to measure the speed on the coupling between a motor and a torquemeter. I have a reflective sticker on the coupling, and I’m using this sensor to pick up the speed. However, when I connect the sensor, I’m reading zero on the MC41. I can see the lights on the sensor changing, which indicates the sensor is generating pulses, but the MC41 isn’t registering them.Here’s how I connected the sensor:
Sensor pin 1 (brown): 12V
Sensor pin 2 (white): GND
Sensor pin 3 (blue): C1:12 on the MC41
Sensor pin 4 (black): C1:11 on the MC41
The max speed I want to measure on the coupling is 200RPM. I calculated the max frequency as:
Thus I calculated my Max Frequency (Hz) = (Max RPM×Pulses per Revolution)/60 = (200*1)/60 = 3.33 ~ 3 Hz
Do you have any input on whether the issue might be software or hardware related?
Thanks!