0

Safety COUTs as DOUTs

Kevin 5 months ago in Master modules / MC4x updated by Gustav Widén (System support) 5 months ago 1

We have a project that requires control of multiple cylinders, each cylinder is connected to a double acting valve, 2 separate coils, one for each cylinder movement (in/out). These outputs must be safety in our application.

Reading the instruction manual for the DOUTs on MC43FS, it states we must use only one DOUT HS and one DOUT LS per output when its being used in a safety application, so the controller can switch the valve off by either side in event of a fault. Therefore I have concluded we can only have 5 DOUT safety per MC43FS. Or in other words, 2.5 cylinder valve controls.

Can I instead use COUT, and therefore each cylinder function can be driven by a complete COUT A? For example, i can technically connect 10 cylinders, in/out, i.e. 20 valves? I would have to ensure the current does not exceed the limitations of the groups, but does having the shared COUT + affect the safety aspect of a COUT? There is a note saying all COUTs are safety, and nothing about sharing pins like there is under DOUT so I guess I can overcome my issue of limited DOUTs for safety?


I guess if there was a function other than driving a component in a direction it would not be possible, as you can only drive a COUT in either + or - direction, i.e. not both if you has different valves to energise, which could be at the same time.


Also it explicitly states no diodes on a coil connected to COUT (I guess for regulation), does this still apply if I'm using COUTs digitally, ramping from 0-100% and 100-0%? Would the collapsing digital coil cause damage to the COUT driver?

0

VIN voltage drops

Lars Bolduc 5 months ago in Expansion modules / XC4x updated 5 months ago 0

Hello,

I have an odd issue, maybe power or ground reference related.

XC43 IQAN 6.08, sensors powered using the main 24VDC not regulated VREF.

When I start driving valves with the module the reported voltage from my VIN sensors drops by up to 5%.

It happens to all of them irrespective of the sensor type.

It also jumps around a ton.

This makes a huge difference on my 0-5800 0.5-4.5V sensors.

200+ PSI, not good for sensor accuracy.

Any ideas of what to try to fix?

Regards,

0
Answered

What causes error code VREF error A on MC43?

Richard Shults 6 months ago in Master modules / MC4x updated by Gustav Widén (System support) 4 months ago 3

Image 4541

0

Looking for MD4

TinusXXL 6 months ago in Master modules / MD4 updated 6 months ago 2

Hi, I'm looking to purchase a second-hand MD4 (and XC42) to replace our current control system. Has anyone got these in stock that could be shipped fairly quickly?

Thanks in advance!

0
Under review

XC43 INPUT ERROR

Ethan Zeman 7 months ago in Expansion modules / XC4x updated by Gustav Widén (System support) 6 months ago 2

I am working with a couple customers who are having "No Contact" Issues with XC43s installed to replace XA2s. 

When looking at the XC43 module itself, the error code is 1:2 (one red, 2 yellows).

I'm assuming the module is getting an errant input somewhere which is causing it to shut itself down.

I would like to better understand this error code better.  What causes an input error and under what circumstances does it cause the module to stop communicating with the master.

0
Answered

How does an open load error effect the operation of a PWM HS+LS output.

Kerry Brock 7 months ago in Master modules / MC4x updated by Gustav Widén (System support) 6 months ago 2

I am testing logic with a MC43 and using a PWM HS+LS output.

In the system we are using both sides of the output (+ and -) to drive two individual devices.

Both should never operate at the same time.

To simulate one of the device not operating, we unplug one of the solenoids.

With logic, this automatically causes the other side of the output to now function.

Basically, if the + side fails, it should switch to the - side and operate.

We are getting an open load error on the output with one of the solenoids unplugged and it does not allow us to operate the other solenoid on the PWM HS+LS output.

Is the output designed to shut off both sides if one side detects open load or should the other side work if one side detects open load?

As an example:

Image 4494



If the solenoid between C2:67 and C2:15 is unplugged, but the solenoid between C2:67 and C2:31 is plugged in and fully operational, should we be able to command it with an input signal of -100?

0

Input Ranges for PWM and Accuracy

Daniel Pendleton 7 months ago in Master modules / MC4x updated by Gustav Widén (System support) 7 months ago 2

Is the MC4X PWM Input able to monitor frequency ranges outside of it's normal function like 1000 Hz and if so what would the effects be with the resolution of the readings from the MC4X? 

0
Answered

molex connector cable

theo mastenbroek 8 months ago updated by Gustav Widén (System support) 8 months ago 6

What cable fits the molex connector best? i have tried several cables but somehow the shield is always to thick

0
Answered

MD5 Power capability

Neil Skoog 8 months ago in Master modules / MD5 updated by Gustav Widén (System support) 8 months ago 5 1 duplicate

How current can I draw out pins 56 (bat+) and 29 (bat-) if I am using pins 42(bat+) and 43 (bat-) for the input power. I need to power 2 each IQAN sv120 cameras.

0

What material is used for the molded rear panel of the MD4-10?

jlgeorge 9 months ago in Master modules / MD4 0

What material is used for the molded rear panel of the MD4-10?  I was asked by a customer and couldn't find anything about it in the catalog.