MD4 and hydrogen sulfide (H₂S) exposure
We have experienced issues with two MD4-10 units where the touchscreens have become unresponsive. These master modules were being used on two different underground mining machines, operating in the same area of the mine with high levels of H₂S. Could there be a correlation between H₂S exposure and the touchscreens becoming unresponsive?
MC43 Reports Vref error cannot measure
Good morning. I have and MC43 and MD4 running on a machine that is programmed in 6.08.32. I am getting random MC43 Vref B error codes along with the errors for the switches and transducers connected to that Vref.
When I record a plot graph of the MC43 diagnostic channel attached to the Vref, input voltage, and the input voltages for all the sensors, I am not able to record any change in the voltages that would indicate a Vref issue. Has anyone else ran into this issue?
Driving PVEM Danfoss With IQAN MC43
Hi folks,
Does anyone here have experience with controlling a Danfoss PVEM valve with IQAN?
Danfoss literature is rather scarce, and I am working with a legacy machine, and trying to upgrade the controllers.
What should the signal be going from the MC43 to the PVEM?
Thanks,
XC44 address tag error / no contact
Hi Gustav,
We are experiencing issues with XC44 reporting no contact error and ID tag LED error.
Test bench system consists of the following:
- MD4-10 (6.08.24.8051):
- Adress tag 1
- Can bus A – terminated
- Can bus B – not used
- Can bus C – not used
- Can bus D – not used
- XC44 module:
- Address tag 2 (pin 4 and 20)
- Can bus A – terminated
- XC44 original harness on C1 and C2
- No inputs, no outputs for testing purposes.
- Tried different, known address tags
- C1 pins have been verified.
Pushing the project to the MD4 has not fix the problem. We tried the same setup with IQAN 7 – same results.
Our field service started reporting same issues in the field where the XC44 is reporting no address tag errors.
Touchscreen glove compatibility
We have a customer that requires a certain type of PPE glove to be used when operating MD5 HMI. The system we have planned is using 10" display but we don't currently have a unit here to trial, instead I have tried a MD5-5 with the certain glove type and it works OK.
Is the 10" version just a scaled 5" and therefore I can assume as long as it works with the 5" it will be fine with the 10" version? I guess it depends if the same manufacture and screen tech is shared between the different modules?
Lifetime of MC43FS
We have a project that is to be used for the next 40 years. It is a functional safety system that utilises MC43FS. These modules will likely be superseded multiple times (probably due to enhancements in electronics etc) after the 20 years lifetime shown in the manual:

To guarantee functional safety, presumably its recommended we remove and replace the MC43FS after 20 years as described in the manual regardless if the module is working correctly? I'm trying to avoid re-assessing the system in 20 years time and fitting a safety controller available in 2045. Therefore I intend on having a brand new MC43FS available for when the system needs a replacement module in 2045.
Is the 20 years triggered as soon as the module is powered up, therefore we would need to clone the software only when we want to replace the module in 2045 (rather than installing software now and starting the 20 years timer)? Or has the module 20 years been triggered from manufacturing date on the serial number?
Does any of you know why md3 keeps going over a pre-set angle causing system to dead head?
I already lowered angle and still goes over preset angle. What other setting can cause it to go over.
connecting to iqan system with a cat comm adapter 3 for software update
We have a IQAN R7 software app on our computer. We are trying to communicate with a IQAN software on a Weiler brand machine. It has a CAT ET port that we are supposed to connect to the machine with via a CAT Comm adapter 3. When I go to connect, selecting CAN on the connection page, it gives a error code E126 Unable to load CA3rp32.dll. Please update RP1210 driver to a 64-bit version. I dont know that we have that option to do a RP1210 update.
Terminated or not address tag
Hello,
Where can I read about when to use terminated address tag or not? E.g. 0T and 0 tag? When prototyping discrete resistors may be useful but will it work with just a resistor of correct value? Please advise.
MC2 controller relay protection. Failed MELF resistor DOUT
I have 2 different units both using MC2 DOUT to control a large solenoid. Both have flyback diodes installed correctly near the relay. After several years of use, both have the MELF resistor for that DOUT failed inside the module. How can i prevent this from happening to a new or repaired module? Fire a smaller relay to control the large solenoid? Add a capacitor to the DOUT line? Another diode inline on the DOUT line?